Just a note on the HX location. I chose to install it out on the Garn about 220' from the house for a couple reasons. Number one was the fact that being connected to the house piping in this way, it's all pressurized which makes air elimination a cinch.
Number two is that it allows all the underground piping and nearly all the exposed piping in the "garn barn" to be antifreeze protected along with the house boiler. We never have to think about "what if....." The loop is simply primary/secondary into the return of the house boiler, heating it up before it hits the boiler.
The house system is a combination of Climate Panel and steel panel radiators. The Climate Panel is supplied as a low temp circuit with a motorized mixing valve adjusting the floor temp based on outdoor conditions. The panel rads all have TRV's on them which provide room by room temp control. There is no traditional "thermostat" in the house and we didn't have to make any changes to the house setup or control scheme.The HX is a 10" x 20" - 50 plate. I sized it to get the approach temp as close as possible. In other words, if we're down to say.....125* in the Garn, I can still get nearly the same temp out to the house.