I promise I had a great, witty and informative response to your reply(it even had calculations in it). when I clicked "post" I was informed that I would have to log in. fine. but the post was gone. I'll try to replicate.
the shorter version is that in heating applications, we can harvest between 600 and 700 BTU per square foot of solar hot water panel per day.Longer explanation follows.
a standard solar domestic hot water setup for the midwest is 2 4x8'panels and an 80 gallon tank.
Panels are rated in 5 temperature categories, based on the difference between the working fluid temp and the ambient temp, I'll use a solarskies 32 square foot panel as an example, because I know the numbers by heart. (these numbers are avaliable for any commercially available panel at www.solar-rating.org)
A: panel is 9 deg less than ambient. extremely efficient, say pool heating (85 degrees) in a hot climate (say 94 degrees) not gonna happen too often in the midwest. ss-32 panel produces about 42,000 btu per clear day. or about 1312 btu/sf
B: Panel is 9 degrees warmer than ambient, say pool heating in a mild climate ( 85 panel and 77 deg ambient) still pretty efficient.ss-32 produces about 38,000 btu per day, or 1187 btu per SF.
C: Panel is 36 degrees warmer than ambient (say heating domestic water in a warm climate, 120 panel temp and 84 ambient) Panel producses 32,000 btu per day, or 1000 btu/sf
D panel is 90 deg above ambient (say water heating/space heating, 120 deg on a 30 degree day) panel produces 19,000 btu per day, or 593 btu per SF
and E, panel is 144 deg above ambient ( say water heating/space heating in a really cold climate, or absorbtion air conditioning, panel produces 7000 btu per day, or 218 btu per day per SF.
you can see the efficiency drop off steeply as the panel temps rise. we try to keep solar loop temps under 120 deg in the winter to keep those losses lower.
so a domestic hot water system, with 64 SF of panel area will collect half of it's heat (in the mild summers we have in WI), at category C, and the other half will be closer to category D.
64 sf of panel will give you 32,000 btu for half a day's collection(in cat C), and 19,000 btu for half a day's collecton in category D (as the tank heats up, the solar loop temp increases, and the efficiency decreases) so we can get something like 51,000 btu into that 80 gallon tank.
assuming that all the previous day's production was used up overnight and in the morning, and a starting tank temp of say, 50 degF (or whatever your ground water temp is), that 51,000 btu will get you an 81 degree rise. but there'll be some losses in the heat exchanger, say 10%, so that gets you about 73 degree rise, or 123 degrees. presto, the same temp your water heater was going to heat it to anyway. now you don't need to heat it up any more, and your water heater just sits there idle. nothing wrong with that.
whew. .
by those calculations, dumping that same SF of panel into your 70 degree GARN unit (I'm guessing 70 degrees might be a sensible summer ambient temp?) you'll be in the 0 degrees above ambient temp for your drainback system, so at halfway between -9 and 9 from ambient would get you 40,000 btu per day per panel (and no HX losses). so you'll be dumping 80,000 btu per day into the GARN, and 1850 gallons of water, you'd get about a 5.5 deg rise. and your water heater makes up the difference. that 51,000 btu in the smaller storage tank offsets about 1 gallon of propane at 60% efficiency. (91,000 btu per gallon LP * .60= 54,600 btu)
and in the winter, you're heating that GARN up to 160-180 regularly, and putting your panels into the Cat D range or worse yet, the cat E range (180 deg minus 144= 36 deg ambinent) you'd be getting 218 BTU per SF per day.
this is why we solar installers like Hydronic radiant heat so much. it works at temps down to 85-90 degrees in the best cases, and more like 120 deg in less than optimal cases.
this is where evacuated tube collectors come in. they have a shallower efficiency vs deltaT slope than flatplate collectors. and as far as I can tell they're all made in China. I can get flatplate collectors from less than 300 miles away. I also don't have any good info on long term reliabilty. Sure I'm going to put some up on my place, but I know the flatplates I'm using will last 30 years ( I know people with the same panels that are 30 years old, and working fine)
if you dive into the SRCC (www.solar-rating.org) OG100 info, make sure you're comparing net apeture especially for the evacuated tube collectors.
end of mini lesson. now I need to learn more about GARN performance.